Sunday, 06 July 2025
AN #201 - Fan and temperature controller with LCD Print
Created by Thomas Jensen
The module uses an LM35 sensor for measuring the temperature, it is a pre-calibrated IC with output voltage linearly-proportional to the Centigrade temperature. This is read directly by the internal AVR ADC, and turned into actual degrees with a simple calculation. The fan is powered by an PWM output, giving it variable speed. Set points for the fan and alarm can be adjusted and is saved to EEPROM
Link to original project can be found here
Operation
When the temperature reaches the setpoint; the fan will start on speed 1. After 30 seconds the speed is increased to level 2, unless the temperature has dropped below the setpoint. If the temperature rises above the setpoint speed is set to level 3, which is the maximum. The alarm is triggered if the temperature is equal to the alarm set point for more than 30 seconds. It is possible to override the fan with the override switch, or with an external signal. When overridden the fan speed is increased by 2, meaning if 0 then 2, or if 1 or 2 then 3.
Setpoints
Two values are stored in EEPROM; fan and alarm setpoint. These are non-volatile, meaning that they are not lost if the module is without power. Setpoints are saved to the EEPROM about five minutes after they have been changed, to avoid unnecessary writes. When values are changed but not yet saved, a E is displayed in the right corner if the LCD. The setpoints is adjusted using the (on)-off-(on) switches, one degree at the time.
Formula to calculate temperature
Value * 5
--------- = 'C (+- 0.5)
   10
Input pins
  1. PB3 Fan setpoint +
  2. PB4 Fan setpoint -
  3. PB6 Alarm setpoint +
  4. PB7 Alarm setpoint -
  5. PB5 Override fan switch
  6. PC0 Temperature (Analog)
Output pins
  1. PD0 LCD1
  2. PD1 LCD2
  3. PD2 LCD3
  4. PD3 LCD4
  5. PD6 LCD5
  6. PD7 LCD6
  7. PB0 Lifesignal
  8. PB1 Fan (PWM)
  9. PB2 Temp alarm
D-Sub 9-pin connector
  1. 0V
  2. +5V
  3. Lifesignal
  4. Fan
  5. Temp alarm
  6. LCD background light switch
  7. Override fan switch
Switches
  • (on)-off-(on), fan temp +/-
  • (on)-off-(on), alarm temp +/-
  • on-off, override fan
  • on-off, background light LCD
LEDs
  • Green, Lifesignal
  • Green with lens, fan active
  • Red with lens, temp alarm
LCD
1234567890123456
25C F:30C A:30C*
Fan & Temp Unit!
SW v.2.0
uCtrl.net
System start =)
Source code
' Thomas Jensen | uCtrl.net
' file: AVR_FTU_v_2.0
' date: 15/03/2007
$regfile = "M8def.dat"
$crystal = 1000000
Config Watchdog = 1024
Config Portb.0 = Output
Config Portb.1 = Output
Config Portb.2 = Output
Config Portb.3 = Input
Config Portb.4 = Input
Config Portb.5 = Input
Config Portb.6 = Input
Config Portb.7 = Input
Dim Lifesignal As Integer
Dim W As Word , Volt As Word , Temp As Word
Dim C_vifte1 As Byte , C_vifte2 As Byte , Set_fan As Byte
Dim C_alarm1 As Byte , C_alarm2 As Byte , Set_alarm As Byte
Dim Alarmled As Integer , Cls_timer As Integer , Alarm_timer As Integer
Dim Eeprom_save As Integer , Eeprom_fan As Eram Byte , Eeprom_alarm As Eram Byte
Dim Alarm_timer2 As Integer , Fan_speed As Byte , Temp_timer As Byte
Dim Fan_delay As Integer , Fan_delay2 As Integer
Dim Fan_timer As Integer , Fan_timer2 As Integer
Config Timer1 = Pwm , Pwm = 8 , Prescale = 1 , Compare A Pwm = Clear Up , Compare B Pwm = Clear Up
Ddrb.1 = 1
Ddrb.2 = 1
Pwm1a = 255
Pwm1b = 255
Config Lcdpin = Pin , Db4 = Portd.3 , Db5 = Portd.2 , Db6 = Portd.1 , Db7 = Portd.0 , E = Portd.6 , Rs = Portd.7
Config Lcd = 16 * 2
Config Adc = Single , Prescaler = Auto , Reference = Avcc
Start Adc
Lifesignal = 21
Alarmled = 0
Eeprom_save = 0
C_vifte1 = 0
C_vifte2 = 0
C_alarm1 = 0
C_alarm2 = 0
Cls_timer = 50
Alarm_timer = 0
Fan_speed = 0
Fan_delay = 0
Fan_timer = 0
Temp_timer = 10
'get eeprom values
Set_fan = Eeprom_fan
If Set_fan > 50 Or Set_fan < 10 Then Set_fan = 30
Set_alarm = Eeprom_alarm
If Set_alarm > 50 Or Set_alarm < 10 Then Set_alarm = 32
Cls
Cursor Off
Deflcdchar 1 , 32 , 32 , 32 , 7 , 4 , 6 , 4 , 7 'e-sign
Deflcdchar 2 , 32 , 32 , 32 , 32 , 32 , 32 , 32 , 32 'blank
'turn off alarm
Pwm1b = 0
Locate 1 , 1
Lcd "Fan & Temp Unit!"
Locate 2 , 5
Lcd "SW v.2.0"
Waitms 2000
Cls
Locate 1 , 1
Lcd "uCtrl.net"
Locate 2 , 1
Lcd "System start =)"
Waitms 2000
Cls
Locate 1 , 5
Lcd "F:"
Locate 1 , 11
Lcd "A:"
Locate 2 , 1
Lcd "Fan:"
Locate 1 , 1
Lcd "?C"
'turn off alarm
Pwm1b = 255
Start Watchdog
Main:
'cls timer
If Cls_timer > 0 Then Decr Cls_timer
If Cls_timer = 0 Then
 Cls
 Locate 1 , 1
 Lcd Temp ; "C"
 Locate 1 , 5
 Lcd "F:"
 Locate 1 , 11
 Lcd "A:"
 Locate 2 , 1
 Lcd "Fan:"
 Cls_timer = 50
'check temp
If Temp_timer > 0 Then Decr Temp_timer
If Temp_timer = 0 Then
 W = Getadc(0)
 Volt = W * 5
 Temp = Volt / 10
 Temp_timer = 100
'show set points
Locate 1 , 7
Lcd Set_fan ; "C"
Locate 1 , 13
Lcd Set_alarm ; "C"
'set fan
If Fan_delay = 0 Then Fan_speed = 0
If Temp < Set_fan Then
 Fan_timer = 0
If Temp = Set_fan And Fan_speed <> 3 Then
 Fan_speed = 1
 Fan_delay = 600
 If Fan_timer < 300 Then Incr Fan_timer
 If Fan_timer = 300 Then
 Fan_speed = 2
 Fan_delay = 600
If Temp > Set_fan Then
 Fan_speed = 3
 Fan_delay = 600
 Fan_timer = 300
'fan timers
If Fan_delay > 0 Then Decr Fan_delay
'set fan speed
If Pinb.5 = 0 Then Fan_speed = Fan_speed + 2
If Fan_speed > 3 Then Fan_speed = 3
If Fan_speed = 0 Then Pwm1a = 255
If Fan_speed = 1 Then Pwm1a = 170
If Fan_speed = 2 Then Pwm1a = 105
If Fan_speed = 3 Then Pwm1a = 0
Locate 2 , 5
Lcd Fan_speed
If Pinb.5 = 0 Then
 Locate 2 , 7
 Lcd "F"
'set fan temp
If Pinb.3 = 1 Then C_vifte1 = 0
If Pinb.3 = 0 And C_vifte1 = 0 Then
 C_vifte1 = 1
 Set_fan = Set_fan + 1
 Eeprom_save = 3000
If Pinb.4 = 1 Then C_vifte2 = 0
If Pinb.4 = 0 And C_vifte2 = 0 Then
 C_vifte2 = 1
 Set_fan = Set_fan - 1
 Eeprom_save = 3000
'set alarm temp
If Pinb.6 = 1 Then C_alarm1 = 0
If Pinb.6 = 0 And C_alarm1 = 0 Then
 C_alarm1 = 1
 Set_alarm = Set_alarm + 1
 Eeprom_save = 3000
If Pinb.7 = 1 Then C_alarm2 = 0
If Pinb.7 = 0 And C_alarm2 = 0 Then
 C_alarm2 = 1
 Set_alarm = Set_alarm - 1
 Eeprom_save = 3000
'set main temp_alarm
If Temp >= Set_alarm And Alarm_timer < 300 Then Alarm_timer = Alarm_timer + 1
If Alarm_timer = 300 And Alarmled = 0 Then Alarmled = 6
If Temp < Set_alarm Then Alarm_timer = 0
'alarmled
If Alarmled > 0 Then Alarmled = Alarmled - 1
If Alarmled = 4 Then Pwm1b = 0
If Alarmled = 1 Then Pwm1b = 255
'eeprom save
If Eeprom_save > 0 Then
 Eeprom_save = Eeprom_save - 1
 Locate 1 , 16
 Lcd Chr(1)
If Eeprom_save = 1 Then
 Eeprom_fan = Set_fan
 Eeprom_alarm = Set_alarm
 Locate 1 , 16
 Lcd Chr(2)
'show timers
Locate 2 , 15
Alarm_timer2 = Alarm_timer / 10
Lcd Alarm_timer2
Locate 2 , 9
Fan_delay2 = Fan_delay / 10
Lcd Fan_delay2
Locate 2 , 12
Fan_timer2 = Fan_timer / 10
Lcd Fan_timer2
'lifesignal
If Lifesignal > 0 Then Lifesignal = Lifesignal - 1
If Lifesignal = 6 Then Portb.0 = 1
If Lifesignal = 1 Then Portb.0 = 0
If Lifesignal = 0 Then Lifesignal = 21
Reset Watchdog
Waitms 100
Goto Main
Schematic drawing